Tendon utilisation = 0
SOFiPLUS / SSD: Tendon utilisation = 0 – Prestressing appears not to be taken into account
Hello everyone,
I have modelled a prestressed concrete girder bridge using SOFiPLUS and am experiencing problems with the analysis and the consideration of the prestressing tendons in the design.
1. Model description
The structure consists of five longitudinal girders, each with four prestressing tendons. The cross-sections of the girders are larger in the support regions than in the spans. The transition between the different cross-sections is modelled using haunches (variable-depth sections).
2. Prestressing tendon modelling
The prestressing tendons were modelled using spline geometry along the respective girder axes. The haunch geometry is also taken into account in the tendon profiles by means of the “U-offset” and “V-offset” parameters.
The tendons are stressed alternately from the left and right ends. The prestressing forces have been defined, and prestressing steel according to EN 1992 has been selected as the material.
3. Loads and analysis
All other loads are applied to the structural model in SOFiPLUS. Traffic loads are applied via SSD, where the load combinations are also generated.
The analysis produces the following warnings:
+++++ Warning No. 70413 in program BBMI
Cross-section 114: No convergence
Element 10188 X= 0.333 LF 3 ITER 326 IER -1 -3
+++++ Warning No. 211 in program AQBBMQ
Shear design unsuccessful at 34 sections
4. Problem description
The design results show a tendon utilisation of 0. Consequently, the overall cross-section utilisation appears to exceed the permissible limit.
The curvature loads of the prestressing tendons are visible in the Viewer. I therefore assume that the tendon profiles are generally present in the model. However, I cannot determine whether the prestressing forces are actually being taken into account correctly in the structural analysis and the subsequent design.
5. Questions
  • What could cause the tendon utilisation to be reported as 0?
  • Is the fact that the curvature loads are visible in the Viewer sufficient to confirm that the prestressing has been correctly transferred to and considered in the structural analysis?
  • Which settings should I check regarding the tendon definition, prestressing forces and load combinations in SSD?
  • Could warning 70413 (“No convergence” for the cross-section) and the unsuccessful shear design (warning 211) be related to the apparent lack of consideration of the prestressing tendons?
I would appreciate any suggestions on which settings or result evaluations I should check to identify the cause of the problem.
Thank you in advance for your help!
5
Hi Johanna,
I try to answer your questions or to give some hints.
  1. What could cause the tendon utilisation to be reported as 0?
    => Where do you see this? In Report of AQB? Somewhere in Graphic? Which load case?..
  2. Is the fact that the curvature loads are visible in the Viewer sufficient to confirm that the prestressing has been correctly transferred to and considered in the structural analysis?
    => No, this is only a hint that the prestressing is defined. If it is considered correctly in further calculation you have to check seperately.
  3. Which settings should I check regarding the tendon definition, prestressing forces and load combinations in SSD?
    => Do you know the videos under
    https://www.youtube.com/watch?v=6Oqp-2p0cZA&list=PLkNZCJG1CDyPJeKGCyGzUEz3QzG54QXIj
    I think there you find some hints. Without exact knowledge about the problem I cannot give you better tipps.
  4. Could warning 70413 (“No convergence” for the cross-section) and the unsuccessful shear design (warning 211) be related to the apparent lack of consideration of the prestressing tendons?
    => No, I don’t think so. This is only a hint about iteration problems.
    Below you will find a kind of AQB troubleshooting guide describing what can be done when this warning appears.
____________________________________________________________
Under consideration of a strain variation AQB tries to calculate the necessary reinforcement. Depending of the number of reinforcement layers it’s possible that there isn’t a well-defined solution.
You have several possibilities to get to aim:
  1. The number of defined reinforcement layers should be kept as few as possible in AQUA.
  2. To take the torsion, one should consider one circumferential reinforcement layer as one optional reinforcement layer (Z-layer), and set its torsion contribution to “ACTI” (e.g with single reinforcement at the corners) in AQUA
  3. Other layers should be best defined as minimum reinforcement (M-Layer) with their torsion contribution set to PASS in AQUA.
  4. Try to isolate the beam element where the convergence couldn’t be reached and handle it explicitly by imposing it under its corresponding internal forces in AQB.
    4.1 Consequently one can check the stress distribution in the cross section through Resultviewer.
    5.To limit the acceptable iterative range of reinforcement in a cross section in AQB, try to define a reasonable minimum and maximum reinforcement in AQUA.
  5. One can also manage the behavior of the internal algorithm and convey it to better convergence by for example using “REIN P7 10” in AQB.
  6. One may define a smaller precision for determination of the internal stresses with e.g “ctrl ETOL 0.01”.
  7. You can limit the strain range in DESI-sentence with the input of C1 to Z2 (s. AQB-manual)
  8. Sometimes the problem is that the cross section is not actually loaded sufficiently. Therefore, there couldn’t be a valid solution for this case. A reasonable input of minimum reinforcement through “DESI AM1 .. AM2 .. AM3 .. 0.1” could be then helpful.
  9. Try to improvise and modify around with the parameters pointed in item 5 to 9.
  10. In the case of composite cross section, we recommend to define a reasonable estimation of the reinforcement as minimum reinforcement in AQUA. The design should be then carried out in AQB using “CTRL REIN FIX”
  11. Try to separate the structural group and elements in different AQB-run, as a solution to one could result to divergence in another group.
I hope this helps.
Regards,
Jost
Dear Jost,
Thank you for your reply and for your advice on how to solve the problem.
  1. The utilisation value of 0 for the prestressing tendons is displayed in the graphical results under Design → Members → Utilisation → Members → Utilisation of reinforcement/prestressing steel stress.
    The load case is design case 2121: “desi BEAM-MY_Q-MXX_SPRI-P_PX”.
Thank you also for the tips regarding the convergence problem. I will try to resolve it by following your recommendations.
Unfortunately, the utilisation of my prestressing steel is still displayed as 0.
Could you perhaps give me any further advice on what might be causing this issue?
Thank you again for your help.
Best regards Johanna
Dear Johanna,
sorry, but “Design → Members” is not existing in Graphic.
I need a clear description to understand what you mean. And to help you efficiently I need the prepaired dataset.
Jost
Dear Jost,
Thank you so much for you answer.
The clear description is: Design → Beam Elements → Utilisation level → Beam elements, Utilisation level σ-s Stress in reinforcements / tendon.
Is this the prepaired dataset that you need:
Variante 1_RICHTIG_exp.dat (3.9 MB)?
Hi Johanna,
the dataset is not runnable. Try it yourself in an empty directory containing only the DAT file. However, based on the TENDON input, I can see that the tendons are indeed intended to be located within the beam elements.
Please take a look at the example “csm31_design.dat” (available in TEDDY under “File → Examples → csm → english → design”) and adapt the workflow used there to your project. In that example, the “CSM” module is used for both the construction stage analysis and the design checks.
Ultimately, the module “AQB” is required for the design of beam elements containing the tendons. The module “BEMESS” included in your dataset is intended for the design of QUAD elements.
You can find further information on the workflow and the design of prestressed concrete bridges here: SOFiSTiK Bridge Design Training
Additional tutorials are available at Bridge Design - SOFiSTiK Tutorials 2026
I hope it helps.
Jost